Replace TMG3200 1+1 Primary With Spare

From TBwiki
Revision as of 15:45, 18 April 2016 by Luc Morissette (Talk | contribs)
Jump to: navigation, search

This procedure does not require system downtime.

Start with the following steps: Prepare for replacement

The replacement of a Primary TMG3200 is comprised of following steps:

Contents

Removing the Defective Unit

  • Shutdown the Primary TMG3200
  • Disconnect from the 1+1 patch panel
  • Disconnect from the VoIP network
  • Disconnect from the Management network
  • Remove the Primary TMG3200 from the equipment rack

Installing the Replacement Unit

Refer to TMG3200 Installation guide

  • Rack-mount the Replacement Unit
  • Connect to the Management Interface
  • Connect to the VoIP Network
  • Connect to the 1+1 patch panel
  • Connect the ETH0 and ETH1 port to the secondary unit

Starting Up the TMG3200

Configuring the replacement unit

  • Once the same version as the secondary unit is installed on this unit, Reset the host role:
  • and configure it as primary:
    • Set primary host role - NOTE: When you are asked if the unit should get configuration and packages from an existing secondary unit, select YES and click Continue.

The configuration database will replicate itself from the secondary unit and will be ready to process calls a few minutes later.